Thread: Drawing plywood sheathing for roof - do you draw perspective

  1. #1
    Scott Townsend Guest

    Drawing plywood sheathing for roof - do you draw perspective

    So if my roof Pitch is 4 in 12 and I'm putting down 4'x8' sheets of plywood.
    do I draw the plywood @ 4' wide or 3.794' wide?

    Thanks,
    Scott<-

    my calcs for 3.794
    Sq(A) + Sq(B) = Sq(C)

    So for a 4 in 12 pitch you have
    Sq(A*3) + Sq(A) = Sq(4)
    9 * Sq(A) + Sq(A) = 16
    10*Sq(A) = 16
    Sq(A) = 1.6
    A = SqRt(1.6)
    A = 1.2649

    A*3 = 3.794

  2. #2
    Paul Turvill Guest
    48^2 - 16^2 = 2048; SQR(2048) = 45.254" = 3.77'

    Most architects and designers with whom I'm familiar don't bother to detail
    every sheet of plywood. If you feel you must, then I suppose you'd want to
    use the 3.77' dimension (or 7.54' for sheets applied perpendicular to the
    ridge). Usually a simple callout will suffice, however.
    ___

    "Scott Townsend" <scott-i@.-N0-SPAMplease.enm.com> wrote in message
    news:422a62b2$1_2@newsprd01...
    So if my roof Pitch is 4 in 12 and I'm putting down 4'x8' sheets of
    plywood. do I draw the plywood @ 4' wide or 3.794' wide?

  3. #3
    Scott Townsend Guest
    I thought as much, though this is kind of my first drawing. Kind of flying
    by the seat of my pants!

    I was just putting on the roof of one structure that happened to be an even
    multiple of 4', then when I went to the other it occurred to me that I'm not
    drawing something that is really in the XY plane.

    My Model set of prints shows 4'x8', but after being photocopied I could have
    lost the .23 (-;

    So then when drawing the roof I guess I really only want to throw on a few
    sheet of plywood and callout the type and placement?

    Thanks!
    Scott<-
    "Paul Turvill" <nospam@turvill.com> wrote in message
    news:422a7137_1@newsprd01...
    48^2 - 16^2 = 2048; SQR(2048) = 45.254" = 3.77'

    Most architects and designers with whom I'm familiar don't bother to
    detail every sheet of plywood. If you feel you must, then I suppose you'd
    want to use the 3.77' dimension (or 7.54' for sheets applied perpendicular
    to the ridge). Usually a simple callout will suffice, however.
    ___

    "Scott Townsend" <scott-i@.-N0-SPAMplease.enm.com> wrote in message
    news:422a62b2$1_2@newsprd01...
    So if my roof Pitch is 4 in 12 and I'm putting down 4'x8' sheets of
    plywood. do I draw the plywood @ 4' wide or 3.794' wide?

  4. #4
    teiarch Guest
    To add to Mr. Turvill's post:

    He might be doing shop drawings? If not, abide by P.T.'s suggestion.

  5. #5
    Scott Townsend Guest
    Funny that you mention Shop Drawings... Yes and no... (-; It is a drawing
    of a shop...a Shop/Garage.

    I've included a PDF of the Elevation Views in the Customer Files Section:
    Titled: Shop-Garage Elevations

    Scott<-
    "teiarch" <nospam@address.withheld> wrote in message
    news:4123301.1110081989899.JavaMail.jive@jiveforum 2.autodesk.com...
    To add to Mr. Turvill's post:

    He might be doing shop drawings? If not, abide by P.T.'s suggestion.

  6. #6
    James Murphy Guest
    MHO, it doesn't matter how you do it the "nail drivers" will do as they see
    fit.

    Murph

    "Scott Townsend" <scott-i@.-N0-SPAMplease.enm.com> wrote in message
    news:422a87fd$1_2@newsprd01...
    Funny that you mention Shop Drawings... Yes and no... (-; It is a
    drawing of a shop...a Shop/Garage.

    I've included a PDF of the Elevation Views in the Customer Files Section:
    Titled: Shop-Garage Elevations

    Scott<-
    "teiarch" <nospam@address.withheld> wrote in message
    news:4123301.1110081989899.JavaMail.jive@jiveforum 2.autodesk.com...
    To add to Mr. Turvill's post:

    He might be doing shop drawings? If not, abide by P.T.'s suggestion.

  7. #7
    Randall Culp Guest
    3D model it.


    "Scott Townsend" <scott-i@.-N0-SPAMplease.enm.com> wrote in message
    news:422a62b2$1_2@newsprd01...
    So if my roof Pitch is 4 in 12 and I'm putting down 4'x8' sheets of
    plywood. do I draw the plywood @ 4' wide or 3.794' wide?

    Thanks,
    Scott<-

    my calcs for 3.794
    Sq(A) + Sq(B) = Sq(C)

    So for a 4 in 12 pitch you have
    Sq(A*3) + Sq(A) = Sq(4)
    9 * Sq(A) + Sq(A) = 16
    10*Sq(A) = 16
    Sq(A) = 1.6
    A = SqRt(1.6)
    A = 1.2649

    A*3 = 3.794

  8. #8
    teiarch Guest
    Murph: That's what construction specifications are for. In Section 06100, Rough Carpentry, you can describe what type of sheathing is to be used, how the sheets are to be oriented, how many fasteners per inch should be provided, and how the sheets are to be placed with respect to each other.

    Since specifications are part of the contract documents, the nail drivers are required to follow them as well as drawings.

  9. #9
    James Murphy Guest
    I won't argue that, but as a former nail driver those pieces of paper
    usually get put behind a truck seat and stay there.

    Murph

    "teiarch" <nospam@address.withheld> wrote in message
    news:15109078.1110160842034.JavaMail.jive@jiveforu m1.autodesk.com...
    Murph: That's what construction specifications are for. In Section
    06100, Rough Carpentry, you can describe what type of sheathing is to be
    used, how the sheets are to be oriented, how many fasteners per inch
    should be provided, and how the sheets are to be placed with respect to
    each other.

    Since specifications are part of the contract documents, the nail drivers
    are required to follow them as well as drawings.

  10. #10
    Martin Shoemaker Guest
    Murph,

    I have to agree. When we did the office addition at my house the
    framers did almost all their layout using just a piece of string. The
    one thing they measured was the existing hip roof pitch over the garage,
    which they used for the new trusses. The trusses had to match up with
    the hip roof on the front porch. Conventionally framed house. 4:12
    pitch on the garage, 3.5:12 on the porch. They also left the roof open
    on two weekends when we had major rain storms. Lots of water damage to
    the rest of the house.

    Similar with the stucco contractor. We had specified a three coat
    system to match the 35 year old existing stucco. The contractor did
    "western one coat". When we complained his reply was, "That's what we
    do."


    Martin


    James Murphy wrote:
    I won't argue that, but as a former nail driver those pieces of paper
    usually get put behind a truck seat and stay there.

    Murph

    "teiarch" <nospam@address.withheld> wrote in message
    news:15109078.1110160842034.JavaMail.jive@jiveforu m1.autodesk.com...

    Murph: That's what construction specifications are for. In Section
    06100, Rough Carpentry, you can describe what type of sheathing is to be
    used, how the sheets are to be oriented, how many fasteners per inch
    should be provided, and how the sheets are to be placed with respect to
    each other.

    Since specifications are part of the contract documents, the nail drivers
    are required to follow them as well as drawings.


  11. #11
    teiarch Guest
    Murph & Martin: Agree with your comments to a point.....Only thing is that IF you have it in the contract (via specifications) you have a much stronger case for recovering damages than the usual ",,,per plans and specs..." language. Doesn't mean that the things both of you mentioned won't still happen but you have a much stronger case when the lawyers get involved.

  12. #12
    Martin Shoemaker Guest
    We had the appropriate language. The problem is/was that there's so
    much construction activity here that workmanship takes a back seat to
    getting to the next job. As far as I'm concerned the work is shoddy,
    but if I pursued it the response I'd get would be that the work meets
    prevailing standards for the area. I'll looking at a bathroom door at
    the moment. On the latch side the stop touches the door at the bottom,
    but there's a 3/8" gap between the stop and the door at the top. This
    is considered "good enough" here. I could have gone to the Registrar of
    Contractors, but the best I'd get there would be instructions to the
    contractor to fix things. If they can't do it right the first time why
    should do better the second time? And lawyers, why? The lawyers are
    the only ones to win when you sue on a project with a $70K total cost.

    If I ever build again I want to find a master carpenter who's
    semi-retired who will do the entire job himself. And, at the risk of
    being politically incorrect, require all workers to speak English fluently.

    Martin

    teiarch wrote:
    > Murph & Martin: Agree with your comments to a point.....Only thing is that IF you have it in the contract (via specifications) you have a much stronger case for recovering damages than the usual ",,,per plans and specs..." language. Doesn't mean that the things both of you mentioned won't still happen but you have a much stronger case when the lawyers get involved.

  13. #13
    Homerloew Guest
    The biggest problem is that anyone who can pick up and swing a hammer calls themselves a builder. Even the butchers (what I call bad builders) can find a few "good" references. The only way to make sure you have a good builder is to look at his work, and more than one job. If he can't take you to at least 10 jobs at various stages, dump him.

    I will take you to every job I have ever done, pride in you work, that is what is missing.

    As far as some of the other discussions about drawing roof plywood to exact scale or calling out in specs, what a waste of time. What should be done is find a good builder, one that has a proven reputation. EVEN IF IT COSTS A LITTLE MORE. But there is another problem, we want everything done so cheap.

    I could drive a Neon, but I drive a 300M because it IS a better car. You can hire a butcher, or you can hire a builder.

  14. #14
    teiarch Guest
    Martin: I know where you're coming from with the "...meets prevailing standards..." argument. It's the same "housebuilder mentality" I see all the time.

    If you have the language in the contract, you're setting the "standard" for your project regardless of what is deemed the local standard. You're on firm legal ground if you have the time to pursue it. Unfortunately, most just shrug their shoulder and let the SOBs get away with it.

Similar Threads

  1. Perspective View
    By perecy in forum SolidWorks
    Replies: 2
    Last Post: 09-21-2005, 05:10 PM
  2. eDrawings and Perspective
    By John Eric Voltin in forum SolidWorks
    Replies: 0
    Last Post: 04-12-2005, 08:52 AM
  3. IV User's Perspective of SWW
    By Sean Dotson in forum SolidWorks
    Replies: 6
    Last Post: 02-04-2005, 05:45 PM
  4. save as tif in perspective for WF?
    By warrenginn in forum Pro/Engineer
    Replies: 2
    Last Post: 12-20-2004, 12:38 PM
  5. 1,2,3-perspective and cabinet projection
    By tuisu in forum AutoCAD
    Replies: 1
    Last Post: 12-08-2004, 09:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Other forums: Access Forum - Microsoft Office Forum - Exchange Server Forum